All Tests goes in in bad State

All questions related to installations, configurations and maintenance of Advanced Host Monitor (including additional tools such as RMA for Windows, RMA Manager, Web Servie, RCC).
Post Reply
I_AM
Posts: 7
Joined: Wed Mar 02, 2011 10:19 am

All Tests goes in in bad State

Post by I_AM »

Hi, i have defined 3 SNMP Trap Tests

1. Humidity goes over 80%
2. Temperature goes over 50 Grade Celsius (Warning High)
3. Sensor is online or not

Now when the Temperature exceeds 50 Grade Celsius, the Trap 2. goes in State "Bad"

but the other two Traps goes in Bad State too ??

In "Test Properties" the Field "Synchronize Counters" ist marked and gray deposited !? Is here the Problem ?

thanks in advance

Edit: Now i have deactivated the "Synchronize Counters" field but the Problem is not solved :cry:
KS-Soft Europe
Posts: 2832
Joined: Tue May 16, 2006 4:41 am
Contact:

All Tests goes in in bad State

Post by KS-Soft Europe »

"Synchronize Counters" option is related only with Master/Detail tests, it has nothing to do with SNMP TRAP test type.
I assume, problem is in SNMP Trap filter configuration.
If temperature trap message pass SNMP filters of Test1 and Test3, they will get "Bad" status too.
You should check settings of filters for your SNMP trap tests.
Please check the manual or visit our web site for more information at:
http://www.ks-soft.net/hostmon.eng/mfra ... trapfilter